BS 7430 resistance to earth 1

Status
Not open for further replies.

Pgee630

Electrical
Dec 13, 2019
27
0
0
GB
Hi,

May I seek some advice regarding BS 7430 requirement on resistance to earth.
I see in Annex A regarding legislation (the Electricity Supply Regulations), it states resistance to earth has to < 1 ohm. I think it's referring to TN-S system.

But how about TT system?

And how about the HV (or MV) side, if a HV or MV substation is built on-site?

I also can't find a required value for the telecom earth resistance, is it covered in another BS standard?

Thanks
P
 
Replies continue below

Recommended for you

No such a limit for earth resistance it is now required. See BS 7430 A2 Legislation.
. In BS 7671 the maximum earth fault loop impedance is limited for different earth fault system protection.
See Regulation 411.3 Requirement for fault protection
In Table 41.5 it is a note that the maximum recommended earth resistance has to be less than
200 ohm.

©
BS_7430_A2_LEGISLATION_ywwtzy.jpg
 
Hi,

I've always been against the maximum earth resistance value (except for EMC). In terms of safety, and especially for MV systems, the maximum value is dictated by step and touch potentials permissible limits.

For TT systems the earth resistance does not really matter as long as residual circuit devices are used.
By the way, is there any table giving the maximum permissible touch voltage in function of time ?

Rgds
 