Hi all
i have a question about buckling lenght factor for steel column.
i have Building which is 9 storys height with moment resistant frame(MRF) on one direction and bracing on the other direction both are for lateral loads resistance.
There is a column which is a part of the moment resiatnce frame and on the other direction it is supported by X bracing and a steel beam at floor level(shear connection)
so i have assumed buckling lenght factor for column in direction of X bracing to be 1.
and i calculated buckling lenght factor for the column in the direction of the moment resiatnce frame using Aligment charts.
The column is hinged on base. I got K=3.5!!
First question. Using K factor=1 for direction of bracing is ok?
Second Question, i do not feel ok by using Kfactor=3.5! in direction of moment resiatnce france because this will lead to extremely big section. so shall i assume K factor on MRF direction=2?
Thanks All
i have a question about buckling lenght factor for steel column.
i have Building which is 9 storys height with moment resistant frame(MRF) on one direction and bracing on the other direction both are for lateral loads resistance.
There is a column which is a part of the moment resiatnce frame and on the other direction it is supported by X bracing and a steel beam at floor level(shear connection)
so i have assumed buckling lenght factor for column in direction of X bracing to be 1.
and i calculated buckling lenght factor for the column in the direction of the moment resiatnce frame using Aligment charts.
The column is hinged on base. I got K=3.5!!
First question. Using K factor=1 for direction of bracing is ok?
Second Question, i do not feel ok by using Kfactor=3.5! in direction of moment resiatnce france because this will lead to extremely big section. so shall i assume K factor on MRF direction=2?
Thanks All