Boiler106
Structural
- May 9, 2014
- 211
I have a 5-story block and plank residential building in the US, IBC 2018, Seismic Design Category C.
Each apartment unit will have masonry divider (shear) walls and the corridors will have masonry shear walls in a portion of the length.
We're trying to locate the building expansion joints. Tech Digest 65 says we can span 277 ft for our location.
Ideally, I would put them in the four corners of the building but the Architect will likely object.
I'm looking for input from others. Would there be a reason to object to the two locations shown in the graphic?
I usually try to avoid L, T and U shaped structures (or at least limit the length of the outstanding wing) per this article: AISC Modern Steel Steelwise 2011.
Each apartment unit will have masonry divider (shear) walls and the corridors will have masonry shear walls in a portion of the length.
We're trying to locate the building expansion joints. Tech Digest 65 says we can span 277 ft for our location.
Ideally, I would put them in the four corners of the building but the Architect will likely object.
I'm looking for input from others. Would there be a reason to object to the two locations shown in the graphic?
I usually try to avoid L, T and U shaped structures (or at least limit the length of the outstanding wing) per this article: AISC Modern Steel Steelwise 2011.