Built-up steel column

ecomarazamy

Structural
Mar 5, 2025
1
I am trying to strengthen the base of a steel column only about 1.5' from the base. I have added WT connection plates to the HSS column on the top and bottom (required).
I found aashto section 6.9.4.3 which provides compressive strength but I can't find anything on the flexural resistance. Any advice on this?
 
Replies continue below

Recommended for you

See section 6.9.2.2 for columns with combined axial compression and flexure.

The definition for the moment capacity (Mrx & Mry) will direct you to 6.10, 6.11, or 6.12 to calculate the capacity.

You can use equation 6.9.2.2.1-3 to check the combined demand to capacity ratio, whether the elements are compact or not, but if you want to use the less conservative equations for combined effects (Equations -1 or -2), you'll have to go through applicable provisions listed in the first bullet point to check if the elements are compact.
 
Last edited: