keyPitsimplE
Structural
A client wants to strengthen a 16' long roof beam by adding section to the bottom (aside from all the other ways it can be done). 7' roof trib. w/ 15 psf DL and 25 psf SL. Existing 4x10 DF2 is under-designed, so placing a 4x6 DF2 under it will create an adequate section. I = 936 in4.
I found the location (2' from the end) where the moment capacity of the orig. 4x10 exceeds the design moment. I'll start my built up section there. Starting at 0' seems unnecessary and the shear flow there is really high. The shear in the beam is 1754 lb at 2'. Q = 3.5" X 5.5" X 4.625" = 89 in3. VQ/I = 167 lb/in.
I move to 4' from end, V=1169, so VQ/I = 111 lb/in. At 6' it is 56 lb/in. At 8' it is 0. I can acheive these loads with split rings spaced as needed. I'll jack the beam to 0 defl. prior to installing.
Are my numbers and methodology correct? Not sure about Q.
If we decided to use a steel plate on the bottom instead, with SDS screws, could someone share the proper way to do the calcs with transformed the sections?
I know this is a lot, but I also wondered about using a steel tension rod on the bottom, in a 'V' shape, anchored at the ends and held off with a steel post at the center. I would love to see a design example of this old school bridge technique.
Thank you very much in advance.
I found the location (2' from the end) where the moment capacity of the orig. 4x10 exceeds the design moment. I'll start my built up section there. Starting at 0' seems unnecessary and the shear flow there is really high. The shear in the beam is 1754 lb at 2'. Q = 3.5" X 5.5" X 4.625" = 89 in3. VQ/I = 167 lb/in.
I move to 4' from end, V=1169, so VQ/I = 111 lb/in. At 6' it is 56 lb/in. At 8' it is 0. I can acheive these loads with split rings spaced as needed. I'll jack the beam to 0 defl. prior to installing.
Are my numbers and methodology correct? Not sure about Q.
If we decided to use a steel plate on the bottom instead, with SDS screws, could someone share the proper way to do the calcs with transformed the sections?
I know this is a lot, but I also wondered about using a steel tension rod on the bottom, in a 'V' shape, anchored at the ends and held off with a steel post at the center. I would love to see a design example of this old school bridge technique.
Thank you very much in advance.