I am developing a simple spreadsheet to calculate the compressive resistance (Pr) of a built-up wood post according to CSA O86:19. Everything up to 5ply's makes sense, and my calculations match the tabulated values provided in the 2020 Wood Design Manual for built-up columns (the unbraced ones).
I am trying to determine an appropriate way to calculate 6-8ply posts that is code compliant, but I'm running into a bit of a wall.
Any code references herein will be for O86:19, older editions may have different numbered clauses. Any calculations mentioned below have been performed assuming dry service conditions, SPF No 1/2.
6.5.5.4 deals with built-up compression members, and 6.5.5.4.1 outlines that for 2 to 5ply built-up members you can use the following procedures, and take the greatest resistance:
If the post is free-standing, then proceeding with 6.5.5.4.2-6.5.5.4.4 governs.
Now, for a 6ply post, it looks like I am to use 6.5.5.4.5 - Built-up compression members as simple compression members. For a free-standing post this poses a large issue, whereby the capacity of a 3m long 6ply 2x6 is 1.92kN, and thus the overall strength is 11.55kN. For reference, a 4ply post calculated in accordance with 6.5.5.4.2 is good for 94kN.
Further to this, 6.5.5.4.5 says that the calculations are to be performed considering all ply's as independant; the slenderness ratio of the weak direction quickly exceeds 50 when we do not rely on the other ply's for bracing. So my 3m 6ply 2x6 mentioned above technically doesn't pass the slenderness ratio < 50.
I'm curious as to what the members of this lovely forum have considered as reasonable when dealing with these larger built-up posts.
I am developing a simple spreadsheet to calculate the compressive resistance (Pr) of a built-up wood post according to CSA O86:19. Everything up to 5ply's makes sense, and my calculations match the tabulated values provided in the 2020 Wood Design Manual for built-up columns (the unbraced ones).
I am trying to determine an appropriate way to calculate 6-8ply posts that is code compliant, but I'm running into a bit of a wall.
Any code references herein will be for O86:19, older editions may have different numbered clauses. Any calculations mentioned below have been performed assuming dry service conditions, SPF No 1/2.
6.5.5.4 deals with built-up compression members, and 6.5.5.4.1 outlines that for 2 to 5ply built-up members you can use the following procedures, and take the greatest resistance:
- 6.5.5.4.1 - Use the clauses below, or the combined factored resistance of the individual pieces taken as independant members.
- 6.5.5.4.2 - Nailed built-up compression members
- 6.5.5.4.3 - Bolted built-up compression members
- 6.5.5.4.4 - Split-ring-connected built-up compression members
If the post is free-standing, then proceeding with 6.5.5.4.2-6.5.5.4.4 governs.
Now, for a 6ply post, it looks like I am to use 6.5.5.4.5 - Built-up compression members as simple compression members. For a free-standing post this poses a large issue, whereby the capacity of a 3m long 6ply 2x6 is 1.92kN, and thus the overall strength is 11.55kN. For reference, a 4ply post calculated in accordance with 6.5.5.4.2 is good for 94kN.
Further to this, 6.5.5.4.5 says that the calculations are to be performed considering all ply's as independant; the slenderness ratio of the weak direction quickly exceeds 50 when we do not rely on the other ply's for bracing. So my 3m 6ply 2x6 mentioned above technically doesn't pass the slenderness ratio < 50.
I'm curious as to what the members of this lovely forum have considered as reasonable when dealing with these larger built-up posts.