richburton
Specifier/Regulator
- Dec 11, 2009
- 19
I am reviewing plans for a 900 sq.ft. shooting shelter to be located in the flood plain.
The Civil Engineer has provided calculations to demonstrate that the concrete pad will not float away when submerged under flood water.
Here is my question:
What is it that determines the soil depth associated with the buoyant uplift?
He has the uplift calculated as being = Unit weight of water 62.4 pcf x 3 ft x 900 sq.ft. = (-) 168,480 lbs.
The depth of buoyant uplift from the saturated soil below - appears to be equal to the depth of water above the grade line (3 ft).
Thanks. I'm always trying to learn something new.
The Civil Engineer has provided calculations to demonstrate that the concrete pad will not float away when submerged under flood water.
Here is my question:
What is it that determines the soil depth associated with the buoyant uplift?
He has the uplift calculated as being = Unit weight of water 62.4 pcf x 3 ft x 900 sq.ft. = (-) 168,480 lbs.
The depth of buoyant uplift from the saturated soil below - appears to be equal to the depth of water above the grade line (3 ft).