Burden Ratings on ANSI Voltage Transformers for Metering 1

Status
Not open for further replies.

SSLA

Electrical
Dec 6, 2004
37
Folks:

ANSI has defined a number of standard burdens (W,X,Y,Z,ZZ and sometimes M). Usually a VT nameplate will list all that it can support e.g. 0.3WXY for a 75 VA unit and 0.3WXYZ for a 200 VA unit.

But what does it mean if the name plate on a VT with one secondary lists only one value, e.g. 0.3Z? I have always assumed that meant it was also passed factory tests at all of the lesser burdens, i.e. 0.3Z would mean 0.3 class accuracy at W,X and Y burdens as well.

Am I right? Or can accuracy at the lesser burdens exceed the limits of the 0.3 (in this case) class?

I've had a look in the ANSI, IEEE standards and Handbook for Electricity Metering but cannot find a clear reference to what the single rating means.

Can anyone help?
 
Replies continue below

Recommended for you

The correct way to list it would be 0.3 WXYZ, but 0.3Z means the same thing, i.e. 0.3 for burdens up to Z (200 VA).

 