I was asked to evaluate a lawsuit in which our company was named by the owner of a plastics plant whom claimed that we had undersized a major feeder due to very high local soil rho values. After looking at all the data, I determined this was not the cause, but the vagueness of the soil resistivity issue caused such confusion we almost lost the case. It turned out that an inexperienced installer, omitted a pull box and tried to pull six sets of 500kcmil conductors about a thousand feet, through four ninety degree bends and stressed the insulation to point of failure, but they hired a thermal resistivity lab whom proved that the local rho was slightly above the 90 degree standard we used. I cannot imagine having to test every single project, but if there are any important installations, especially high voltage and high amperage feeders, I would recommend a test or the concrete encased duct bank solution. Another thing this does, (I specify 3" seperation between ducts), is provide adequate spacing so that the ducts do not radiate added heat to each other in multiple conduit banks. We had specified concrete encasement, but the owner deleted it for cost reasons. That in itself got our legal fees payed.