Oct 10, 2006 #1 wonderchi Electrical Aug 24, 2006 36 0 0 AU Hi, Should the fault results be the same if i use these two methods: 1. bus admittance matrix 2. hand calc by using Thevenin equivalent sequence circuits Thanks
Hi, Should the fault results be the same if i use these two methods: 1. bus admittance matrix 2. hand calc by using Thevenin equivalent sequence circuits Thanks
Oct 10, 2006 #2 KJvR Electrical Feb 20, 2006 56 0 0 AU Yes, for all three phase balanced faults. Your bus admitance matrix for unbalance faults will have to be compiled from an equivalent sequence component circuit or using Modal domain to decouple the impedances. Upvote 0 Downvote
Yes, for all three phase balanced faults. Your bus admitance matrix for unbalance faults will have to be compiled from an equivalent sequence component circuit or using Modal domain to decouple the impedances.