Bus admittance matrix vs hand calc

Status
Not open for further replies.

wonderchi

Electrical
Aug 24, 2006
36
0
0
AU
Hi,

Should the fault results be the same if i use these two methods:

1. bus admittance matrix
2. hand calc by using Thevenin equivalent sequence circuits

Thanks
 
Replies continue below

Recommended for you

Yes, for all three phase balanced faults. Your bus admitance matrix for unbalance faults will have to be compiled from an equivalent sequence component circuit or using Modal domain to decouple the impedances.
 