Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

bus bar short circuit current capacity & support design

Status
Not open for further replies.

bab1

Civil/Environmental
Jan 11, 2006
1
Can anybody tell me how to calculate the short circuit current carrying capacity for bus bars & how to calculate busbar support distance in a switchboard. For 1000A, 50kA at 50°C what is is the preffered bus bar size if they are mounted edgewise.Kindly advice also if there is some software available for this purposes.

Thanks
 
Replies continue below

Recommended for you

bab1,
I found some useful info in the Copper Development Association's site & they have a CD for applications
Here's the link :hope it helps
 
Suggestions:
1. Check the more officical documentation: Standards, e.g.
1. NEMA BU-1 Busways
2. NEMA BU-1.1 General Instruction for Proper Handling, Installation,
Operation, and Maintenance of Busways Rated 600 Volts or Less
3. UL Std 857 Electric Busways and Associated Fittings
4. ANSI/IEEE C37.20 Switchgear Assemblies Including Metal-Enclosed Bus
5. ANSI/IEEE C37.23 IEEE Standard for Metal-Enclosed Bus and Calculating Losses in Isolated-Phase Bus
6. ANSI/NFPA 70 National Electrical Code
7. Visit
8. Search this Forum. There are some excellent postings already
 
You can use DIN VDE0103. It is about Mechanical and thermal short circuit strength of electric power installations.
You can also find in a Switchgear Manual published by ABB in Germany
 
bab1, as addition to the other mails,I know that each manu
facturer has it's own calculation for the diferent types of
swithdoad,presented in the table form for convenience.
For example, Schneider Electric in it's catalog for PRISMA P swchb proposes for 1000 A 1 bar/per phase with cross-section 80x5 mm for IP < 30 and 2 bars/phase with cross-section 50x5 for IP>31 - for 35C, for the higher temp.up to 50C derate 12% for IP 20 and 15% for IP 54.
The max.distance between busbar support center will be 125 mm. for 1 busbar (80x5) for 52 kA/1s ( case IP < 30) and
275 mm for 2 busbars ( IP>31). The distance between centre lines of phases and neutral busbar 75 mm. Other cases are in the catalogue.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor