Bus bar short circuit duration

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
421
If the Incoming breaker can clear the fault within 3 cycles (50 ms), can the bus bar be rated for 3 cycles? Is there any standard (NEC/ANSI) that requires the bus bar to be rated at 1s or 3s.
 
Replies continue below

Recommended for you

Equipment bus bracing fault duration is generally based on relevant NEMA or ANSI standard. With a 3 cycle rating (standard for MCCs for example), clearing within 3 cycles is possible but will limit ability to coordinate with downstream molded case breakers or fuses. Longer durations can be specified - if manufacturer is willing to provide.

NEC doesn't have any requirements for this. It only requires that all equipment be operated "within its rating".
 