Bacon4Life said:
If the loads are normally on one of the main buses with the other main bus as the hot standby, Breaker 952 could have a settings group with a low set instantaneous element enabled to isolate the standby bus. If the loads are split between buses, perhaps a setting group for use when the bus differential is out of service?
Do you mean a settings groups in the bus differential relays or a separate relay for the bus coupler like a 351?
I was warned by the older folks when I first started out that splitting the loads across two buses and relying on selector switches to correctly configure all lines into the appropriate bus differential zones would surely lead to a misoperation. Perhaps other have had better luck with dual differential schemes.
They are correct if your bus protection lacks a check zone. Check zone is your best friend. For EM (electromechanical) substations that takes place by having a separate set of relays which sum all the bays into a single zone, and then having another set of relays for zone 1 and yet another set of relays for zone 2 where CTs and trip circuits are selectively assigned to each set of zone relays. (Don't forget to also switch the BF trip circuits as well, if present) In order for a trip to take place, both a zone relay must call for trip
AND the check zone relaying. That way if a misstep in switching causes differential current in either zone to call for a trip, the check zone will prevent any breakers from operating since there is no differential current in the check-zone. Even then things can still go wrong, ie an actual bus fault but the zones were left improperly configured clearing both busses.
All in all with EM relaying its much easier, simpler, cheaper and more reliable to just put both busses into a single zone.
If you really want to run a substation like that 50/50 your best bet by far are numerical microprocessor low impedance differential relays like 487Bs with position indicator switches on the bus isolators. Greatly simplified wiring and everything (zone switching, check-zone ect), is done internally to the relay including BF and electronic lockout if desired.
The 4th option is not having any dedicated bus bar protection- a practice that made single breaker double bus very attractive and very feasible in developing countries. Basically you set a step distance zone 1 that reaches through 10-20% of the shortest outgoing line left of the bus coupler with a 12 cycle delay, and a zone 2 (or another relay, so zone 1) that reaches 10-20% right of the bus coupler also with a 12 cycle delay. Line bays have a no delay zone 1, a 20-25 cycle delay zone 2 and a 65 cycle zone 4. Transformer bays also include delayed step distance elements that look through the bus bar or coordinated directional over-current elements. A fault on a bus causes the bus coupler to clear after 12 cycles effectively splitting the substation electrically in two, and then all the lines attached to the faulted bus clear either via a none relcosing revered zone 3 or remote zone 2 after 20-25 cycles- transformer bays in a similar manner. Times adjusted accordingly if breaker failure is used. Its arguable this method is even more stable then having any type of differential bus protection to begin with. Also this is good backup to when bus bar protection is implemented.
Of note- in this method (and its also been argued for the 3 prior methods, especially during a BF) I would recommend disabling the bus coupler during isolater switching in that if a bus fault occurred as an isolater is making or breaking one could have exceptionally high voltages and currents across the isolater contacts since the coupler is the first to open.
In your case, did these SBDB substations always come with bus bar protection or did they lack it at some point?
Bus maintenance seems at least as often as 1 in 10 years based on our double bus single breaker with breaker bypass substations. In addition to replacing the actual bus, we have had planned outage for PT replacement, structure painting, relay testing, and switch maintenance. A planned full clearance on some of our buses is not possible because of loops fed solely from a single source.
No full clearance- this is on your SBDB stations?