I came across something that did not 'feel right' when reviewing a new installation. 138kV Utility switching station with several large generation sources tied into a ring bus.
There is an upgrade to the bus for new 87B (Bus Differential) relays. New panels, Lock Out Relay, Test Switches, etc. This scheme uses a Primary (Low Impedance) and Back Up (High Impedance Scheme). The protection is via SEL 487B (Primary) and 587Z (Back Up) relays.
The back up scheme (587Z) does everything I would expect. Has independent CT's, wired to relay (86B), 86B shorts CT's, etc. 86B trips all zone breakers (Trip Coil #2) and BLOCKs close, via 86B 'b contact' on associated zone breakers.
The Primary Relay (487B) has more contacts available and trips Trip Coil #1 & #2 directly. What troubles me is that the 487B relay does not trip the 86B to block close on the associated zone breakers. Some of the associated zone breakers are lines connected to generation and use a reclosing scheme that is not inherent to the digital relays internal logic (SEL 321 Series). There is nothing in the schematic to suggest that the 487B sends a block close to the line relaying reclosing scheme or SCADA.
There is a single 86B relay, which also serves as the 86BF in this scheme.
My concern is that the primary relaying (487B) does not at least block close on the associated zone breakers. I don't have the settings for the 487B relay yet, but for sure, there are no other contacts in the close scheme in the associated zone breakers that would replicate the 'b contact' of a normal 86 relay.
I suppose a latched trip on the 487B relay could leave a 'standing trip' on the associated zone breakers (and reset via a push botton on the 487B), but then why have the back up relay trip an 86B?
I can think of all kinds of reasons how the back up protection (SEL 587-High Impedance...Shorted Ct's??) , which trips and blocks close via the 86B relay could be out of service and the primary 487B relay could trip, but block close / reclosing.
There are no SEL Mirrored Bits or 61850 schemes involved. This is all traditional hard wired logic schemes.
At this point, it is easy enough to add a few wires and at least have the Primary Relays trip the 86B for the sole purpose of the block close function.
A request for information has been sent. I am just trying to imagine a reason to not include a 'block close' for a low impedance diff scheme.
There is an upgrade to the bus for new 87B (Bus Differential) relays. New panels, Lock Out Relay, Test Switches, etc. This scheme uses a Primary (Low Impedance) and Back Up (High Impedance Scheme). The protection is via SEL 487B (Primary) and 587Z (Back Up) relays.
The back up scheme (587Z) does everything I would expect. Has independent CT's, wired to relay (86B), 86B shorts CT's, etc. 86B trips all zone breakers (Trip Coil #2) and BLOCKs close, via 86B 'b contact' on associated zone breakers.
The Primary Relay (487B) has more contacts available and trips Trip Coil #1 & #2 directly. What troubles me is that the 487B relay does not trip the 86B to block close on the associated zone breakers. Some of the associated zone breakers are lines connected to generation and use a reclosing scheme that is not inherent to the digital relays internal logic (SEL 321 Series). There is nothing in the schematic to suggest that the 487B sends a block close to the line relaying reclosing scheme or SCADA.
There is a single 86B relay, which also serves as the 86BF in this scheme.
My concern is that the primary relaying (487B) does not at least block close on the associated zone breakers. I don't have the settings for the 487B relay yet, but for sure, there are no other contacts in the close scheme in the associated zone breakers that would replicate the 'b contact' of a normal 86 relay.
I suppose a latched trip on the 487B relay could leave a 'standing trip' on the associated zone breakers (and reset via a push botton on the 487B), but then why have the back up relay trip an 86B?
I can think of all kinds of reasons how the back up protection (SEL 587-High Impedance...Shorted Ct's??) , which trips and blocks close via the 86B relay could be out of service and the primary 487B relay could trip, but block close / reclosing.
There are no SEL Mirrored Bits or 61850 schemes involved. This is all traditional hard wired logic schemes.
At this point, it is easy enough to add a few wires and at least have the Primary Relays trip the 86B for the sole purpose of the block close function.
A request for information has been sent. I am just trying to imagine a reason to not include a 'block close' for a low impedance diff scheme.