Hello,
I would like to learn your opinion on the folllowing.
We have a frequency converter (VFD) for a machine drive application (VFD rated power is approximately 20 MW).
The frequency converter is fed by a transformer converter outdoor located. Teansformer primary voltage is 33 kV.
The transformer is a multi-winding phase shifting transformers for 36 pulse VFD/transformer topology at input. Transformer turn ratio is 1 to 18 (quite high).
The current design is based on bus duct connection between frequency converter and its transformer. The bus duct shall cover distance of less than 30 feet.
The question is what is your experience on this type of connection (bus duct) given the high turn ratio transformer and resulting high number of connections between transformer secondary and VFD ? are there any technical limitations or issues you could identify?
Any orientation is appreciated. I can try and provide complement of information as you would require.
I would like to learn your opinion on the folllowing.
We have a frequency converter (VFD) for a machine drive application (VFD rated power is approximately 20 MW).
The frequency converter is fed by a transformer converter outdoor located. Teansformer primary voltage is 33 kV.
The transformer is a multi-winding phase shifting transformers for 36 pulse VFD/transformer topology at input. Transformer turn ratio is 1 to 18 (quite high).
The current design is based on bus duct connection between frequency converter and its transformer. The bus duct shall cover distance of less than 30 feet.
The question is what is your experience on this type of connection (bus duct) given the high turn ratio transformer and resulting high number of connections between transformer secondary and VFD ? are there any technical limitations or issues you could identify?
Any orientation is appreciated. I can try and provide complement of information as you would require.