Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Bus Rating - IEC 60909

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
396
0
16
NL
Which parameter(I"k or Ith or Ik) from IEC 60909 needs to be considered for Busbar rating?
Most commonly bus bar rating is specified something like 25kA RMS for 1s.
Bus bar has to withstand both the Mechanical stress and thermal stress. Why bus bar rating is mentioned in RMS, though the peak short circuit current (ip) is responsible for Mechanical stress of the bus bar during the fault?
 
Replies continue below

Recommended for you

In my opinion there are indeed 3 different rated currents: Ith [Rated normal current (lr)], another Rated short-time withstand current (Ik) and Rated peak withstand current (lp).
The IEC Standard IEC 60909-0 presents a calculation way of the short-circuit level at the point in which the equipment is located. IEC 62271-1 states the equipment rated
current. See for instance: Schneider Electric _Basic for MV Cubical Design.

 
Status
Not open for further replies.
Back
Top