Technically, the bus limit is 400A, so you would determine the full load amps of each machine connected and when you get to 400A, you are done.
Realistically, people use what's called a "diversity factor" relating to the actual LOAD on the machines and which of them will be operating at the same time. That is something that nobody can help you with, it has to be determined / observed in your specific installation. So having 700A worth of machinery connected to 400A bus may be acceptable in one place because someone KNEW that the Gachunketta machine was never going to operate at the same time as the Mawhozis machine, and all 14 of the Whizbangers are actually never more than 50% loaded at any one time, etc. etc. etc.