Bussman Point by Point AIC Calcs

Status
Not open for further replies.

HYDL

Electrical
Feb 21, 2005
22
I've been evaluating the Point by Point method of AIC calcs that is in the Bussman Fuse book and also indicate in other literature. They have calculation for an f factor and an M factor. I'm trying to figure out where they come up with the M factor (the multiplying factor) 1/1+f.
 
Replies continue below

Recommended for you

Think of "M" as the percent (%) of the available fault current that can travel downstream to a given point on the system.

Where f = some function of length, cable type, voltage, and and available fault current at the "beginning" of a system(in many casees this will be available fault current at the secondary of a transformer)

 
Also note that if all other factors are constant (voltage, available SC, cable type) that M decreases exponentially with cable length.
 
Thanks for responding. I understand the M being a percentage of available fault. What I'm trying to do is disect these formulas to determine how they were derived. All items in the f formula I can account for, but I'm not sure why they add 1 to the f and then take the inverse.
 
Interesting...now you've got me thinking about it...For now, I'm going to guess that 1/(1+f) is some kind of approximation for:

exp^-f(x)

where f is some real value of function f(x) and x > 0.

OR maybe its some kind of approximation for a summing series. I'll check into later this evening...I'm studying for the FE anyway.

 
Any more thoughts on the derivation of the point-by-point formulas?
 
See thread238-172100 for my opinion.

As for your basic question, ask Bussmann.
 