Robert789
Electrical
- Feb 20, 2002
- 34
We have a pole mounted, 200 KVAR per phase, grounded wye capacitor bank on a 12.47 kV rural distribution feeder. During a recent line patrol, it was reported that an audible hum or buzz could be heard around this bank that was 'similar to, but slightly louder than that of a medium sized three phase distribution transformer' (500 - 1000 KVA).
When removed from service, the hum remained until the last unit was taken off line. The crew performing the line patrol changed out each of the capacitors with new units, and put the bank back in service, with the noise immediately returning.
A later check of the removed units with a capacitance meter indicated no problems.
Our primary line is 336 ACSR, with a bank of 437 Amp voltage regulators that is approximately 3 miles upline of the capacitors. Loading is residential and agricultural, with no loads that I would consider unusual. This is the only capacitor bank that I know of on the circuit.
Noone here has ever before encountered a noisy capacitor bank, and an online search has turned up nothing. I thought of harmonics and resonance, but I would expect blown fuses and damaged capacitors to be the symptoms of either of these situations.
Any thoughts on this situation would be appreciated.
When removed from service, the hum remained until the last unit was taken off line. The crew performing the line patrol changed out each of the capacitors with new units, and put the bank back in service, with the noise immediately returning.
A later check of the removed units with a capacitance meter indicated no problems.
Our primary line is 336 ACSR, with a bank of 437 Amp voltage regulators that is approximately 3 miles upline of the capacitors. Loading is residential and agricultural, with no loads that I would consider unusual. This is the only capacitor bank that I know of on the circuit.
Noone here has ever before encountered a noisy capacitor bank, and an online search has turned up nothing. I thought of harmonics and resonance, but I would expect blown fuses and damaged capacitors to be the symptoms of either of these situations.
Any thoughts on this situation would be appreciated.