C-Factors for Galvanized pipe

Status
Not open for further replies.

sprinkle2013

Computer
Aug 1, 2013
8
For a dry system using galvanized piping in nfpa 2007 13 edition is it required to have 120 or 100 c-factor? Also is there anything in nfpa 2010 that also requires the use of 100 c-factor for galvanized piping?
 
Replies continue below

Recommended for you

2013 edition changed galvanized to C100. 2010 and older allows you to use C120 for galvanized. That doesn't mean you can't use 100 or something less for whatever reason.

Travis Mack
MFP Design, LLC
 