Cable ampacity in raceway leaving a cable tray

Status
Not open for further replies.

bikenut44

Electrical
Aug 12, 2011
13
0
0
US
If I use 392.80 to determine the ampacity of the conductors in a cable tray, how do I rate the ampacity if the conductors leave the tray in a raceway for approximately 6' and terminate at a switchboard? Do I need to follow 310.15 for raceway? Is there a maximum distance I can run them in raceway before changing the overall rating?
 
Replies continue below

Recommended for you

In the Canadian Electrical Code there is an exception for runs the lesser of 3 meters or 10% of the total run.
Check your code under Conductor Ampacity.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 