Cable Ampacity in Switchgear

Status
Not open for further replies.

mrg397cs

Electrical
Sep 23, 2003
9
ANSI C37.20.2, section 5.5.5 allows 85 deg C cable temperature. When terminating with 90 deg C cable, should cable ampacity be derated?
 
Replies continue below

Recommended for you

The cable terminations will dictate the temp rating of the conductor. Its probably 75C.
 