Hi all,
I have a situation where low voltage cables are becoming hot, about 60 C at the hottest point in the gear B phase (middle). Customer wants to know if this is normal.
Here's the scenario:
We have to feed a 3000 A gear. We have 600V 750 MCM Nual ACWU90 single conductor armored cable. Manufacturer, see link, set the maximum ampacity of that cable at 785 A.
Cables go from an outside transformer, through a wall to the existing gear. Two cable trays are use and the cables disposition is as follow:
N A B C C B A N
N A B C C B A N
so, there's only 4 cables per phase (4 x 785 = 3140 A). Cable spacing is 1 x the cable diameter and spacers are made of wood. Cables go thru an aluminum plate at the transformer, and a fiber plate in the switchgear. Grounding is at one point only, in the transformer throat.
Contractor did the calculations, but seems to me that we're missing a couple of cables. Using CEC Table 3, I get 670 A max current per cable.
Now, table 5B doesn't apply but 5D does and show a derating factor of 0.74. They disregard the N cables... is it ok to do so?
Using this gives 496 A max per cable. 3000 A / 496A/C = 6 C per phase. I guess someone forgot Table 5D.
I have a situation where low voltage cables are becoming hot, about 60 C at the hottest point in the gear B phase (middle). Customer wants to know if this is normal.
Here's the scenario:
We have to feed a 3000 A gear. We have 600V 750 MCM Nual ACWU90 single conductor armored cable. Manufacturer, see link, set the maximum ampacity of that cable at 785 A.
Cables go from an outside transformer, through a wall to the existing gear. Two cable trays are use and the cables disposition is as follow:
N A B C C B A N
N A B C C B A N
so, there's only 4 cables per phase (4 x 785 = 3140 A). Cable spacing is 1 x the cable diameter and spacers are made of wood. Cables go thru an aluminum plate at the transformer, and a fiber plate in the switchgear. Grounding is at one point only, in the transformer throat.
Contractor did the calculations, but seems to me that we're missing a couple of cables. Using CEC Table 3, I get 670 A max current per cable.
Now, table 5B doesn't apply but 5D does and show a derating factor of 0.74. They disregard the N cables... is it ok to do so?
Using this gives 496 A max per cable. 3000 A / 496A/C = 6 C per phase. I guess someone forgot Table 5D.