nightfox1925
Electrical
- Apr 3, 2006
- 567
Hi electrical folks. I am having a discussion with one of my colleagues regarding the cable sizing and we are on the matter of resolving some technical indifferences.
per NEC, it states that the conductors shall be sized not less than 125% of the full load current. In my way of sizing, I have maintained the 125% compliance. That means I will select a cable ampacity that is having an equivalent ampacity, after I multiply with a derating factor, higher than the 125% x FLA. Example, assuming I have FLA=30A, and my overall derating (temperature + grouping) = 0.50, my cable required ampacity is 30 x 1.25 = 37.5A, If I'm going to choose say #6 (with ampacity =65A) then applying 0.5 derating to it will result to 65 x 0.5 =32.5A which will be less than 37.5A or less than the 125% rule. Hence, a #4AWG (ampacity=85A) is selected which will give a derrated ampacity of 85 x 0.5 = 42.5A
On the other hand my colleague has another way,
Required ampacity = 30/0.5 = 60A, then with this, he may choose #6AWG which is 65A.
However, this will not satisfy the 125% rule since with this size, the cable is (60/65)x100%= 92% loaded or less than the 125% rule.
If I am not in violation of the code, then I would prefer the #6AWG which is costing less. But my question, is the 125% rule be maintained after conductor deration. What is the significance of this 125% rule for my understanding.
Thank you.
per NEC, it states that the conductors shall be sized not less than 125% of the full load current. In my way of sizing, I have maintained the 125% compliance. That means I will select a cable ampacity that is having an equivalent ampacity, after I multiply with a derating factor, higher than the 125% x FLA. Example, assuming I have FLA=30A, and my overall derating (temperature + grouping) = 0.50, my cable required ampacity is 30 x 1.25 = 37.5A, If I'm going to choose say #6 (with ampacity =65A) then applying 0.5 derating to it will result to 65 x 0.5 =32.5A which will be less than 37.5A or less than the 125% rule. Hence, a #4AWG (ampacity=85A) is selected which will give a derrated ampacity of 85 x 0.5 = 42.5A
On the other hand my colleague has another way,
Required ampacity = 30/0.5 = 60A, then with this, he may choose #6AWG which is 65A.
However, this will not satisfy the 125% rule since with this size, the cable is (60/65)x100%= 92% loaded or less than the 125% rule.
If I am not in violation of the code, then I would prefer the #6AWG which is costing less. But my question, is the 125% rule be maintained after conductor deration. What is the significance of this 125% rule for my understanding.
Thank you.