Does anyone have some experience with ERA 69-30 and how their derating factors were derived. I do not have access to this document.
I have modeled some 11kV XLPE cables according to IEC287 and confirmed the values with the cable manufacturer. However, most cable manufacturers refer to ERA 69-30. The IEC287 models provides ampacity levels up to 15% lower than the manufacturer's derating tables that refer to ERA 69-30 Part 3. I will appreciate any thoughts on this. What method/tables is the correct method.
Does anyone have some experience with ERA 69-30 and how their derating factors were derived. I do not have access to this document.
I have modeled some 11kV XLPE cables according to IEC287 and confirmed the values with the cable manufacturer. However, most cable manufacturers refer to ERA 69-30. The IEC287 models provides ampacity levels up to 15% lower than the manufacturer's derating tables that refer to ERA 69-30 Part 3. I will appreciate any thoughts on this. What method/tables is the correct method.