Hello,
With regards to Trimble software for bs7671 cable sizing. I understand that a three phase circuit
(No neutral) is one circuit and this can be achieved by 3 single core cables. Say for a “box” we have 5 single cables in parallel per phase (15 cables total) in Trimble for grouping purposes is this treated as 5 circuits Or 15? I am a little confused because if we have three of these boxes we would need 45 cables(5 per phase,3 phases) and not 15 cables.

Thanks
 
Replies continue below

Recommended for you

If you follow BS 7671 Appendix 4 Table 4C1 Rating factors for one circuit or one multicore or a group of circuits or group of multicore cables it is about of a circuit [2 or 3 phases] single-core or multicore cable.
See NOTE 3:
The same factors are applied to:
-groups of two or three single-core cables
-multicore cables
 