Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Cable Grouping Drating in Cable Trays

Status
Not open for further replies.

MagnusElec

Electrical
Aug 31, 2007
4
Based on NEC 310.15(B)(2)(a) Exception No. 2 and 392.11(A)(1), I've concluded that no derating due to grouping is required for three-conductor 0-600V power cables installed in a cable tray; regardless of the number of cables as long as the fill is not exceeded; in a single vertical layer; and without separation distance.

Is this correct? (The situation is different for medium voltage cables).

Thanks
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor