I'm trying to compare some impedance values between a table that I've found with values that are modeled through a computer program. The cable that I'm considering is 350 MCM 69 kV (Teck90) 3/C. The software that I'm using models it with the following parameters (this is in p.u., based on a 1000 foot run, Base MVA = 10 MVA, and the systems voltage is 600 V),
Software: R = 2.2929 , X = 0.40317 , B = 1.74E-6,
Ro = 2.2314, Xo = 0.2552, Bo = 1.74E-6
From the table that I've acquired, this specific cable has an impedance of (in ohms - based on 1000 ft run),
Positive/Negative = 0.040+j0.047
Zero Sequence = 0.316+j0.170
If I convert the table value to a p.u. value (base KV = 0.6, base MVA = 10 MVA) my values aren't very close at all.
Why do you suggest the difference is so great ?
Thanks in advance