Hi All
Here in Australia we commonly use 'V-90' PVC (thermoplastic) insulated and PVC sheathed power cable for cabling to final equipment, i.e. 3 phase motors, and for cabling to small distribution boards. This cable has a 'maximum operating temperature of 90 degrees"
The standards here tell us the maximum current carrying capacity of V-90 cable is based on the cable operating at a maximum temperature of 75 degrees - not 90 degrees. The standard further tell us that it is allowed to operate the cable at the full 90 degrees as long as the following conditions are met by the installation:
1) The cable is installed in a manner that is not subject to, or is protected against, severe mechanical pressure at temperatures higher than 75 degrees C.
I am trying to determine, practically, what this means, with respect to actual cable installation and what is permitted?
For example, if an insulated and sheathed cable is installed on cable ladder, without any further mechanical protection, and it is supported through its entire length, surely it would comply with these requirements.
To be honest I am struggling to come up with a practical example of cable installation that would not meet the installation requirements to operate the cable at the higher temperature. Can anyone give me some practical examples of installations which would and would not meet the requirements?
Thanks all.
Here in Australia we commonly use 'V-90' PVC (thermoplastic) insulated and PVC sheathed power cable for cabling to final equipment, i.e. 3 phase motors, and for cabling to small distribution boards. This cable has a 'maximum operating temperature of 90 degrees"
The standards here tell us the maximum current carrying capacity of V-90 cable is based on the cable operating at a maximum temperature of 75 degrees - not 90 degrees. The standard further tell us that it is allowed to operate the cable at the full 90 degrees as long as the following conditions are met by the installation:
1) The cable is installed in a manner that is not subject to, or is protected against, severe mechanical pressure at temperatures higher than 75 degrees C.
I am trying to determine, practically, what this means, with respect to actual cable installation and what is permitted?
For example, if an insulated and sheathed cable is installed on cable ladder, without any further mechanical protection, and it is supported through its entire length, surely it would comply with these requirements.
To be honest I am struggling to come up with a practical example of cable installation that would not meet the installation requirements to operate the cable at the higher temperature. Can anyone give me some practical examples of installations which would and would not meet the requirements?
Thanks all.