I am new graduate in electrical, if my question is very simple please forgive me in advance.
I am looking at ontario Electrical safety code, Table 1.
It says for single conductor 300MCM cable the ampacity is 480A (85-90 celcius)
On table 2 it says for 300MCM not more than 3 conductors in cable or raceway the ampacity is 295 (85-90 celcius).
On table 5B correction factors for table 1 it says for 3 conductors in contact the derating factor is 0.85
The question is this :
I am expecting that according tables 1, and 5B on table 2 the ampacity for one multiconductor cable (1c-3#350 MCM) be 480*0.85= 408A not 295A. and why table 2 is needed at all if the procedure for calculation is right.
I think I am missing something between multiconductor cables and single conductors.
Any help and references would be highly appreciated.
Regards,
Newcomer2005
I am new graduate in electrical, if my question is very simple please forgive me in advance.
I am looking at ontario Electrical safety code, Table 1.
It says for single conductor 300MCM cable the ampacity is 480A (85-90 celcius)
On table 2 it says for 300MCM not more than 3 conductors in cable or raceway the ampacity is 295 (85-90 celcius).
On table 5B correction factors for table 1 it says for 3 conductors in contact the derating factor is 0.85
The question is this :
I am expecting that according tables 1, and 5B on table 2 the ampacity for one multiconductor cable (1c-3#350 MCM) be 480*0.85= 408A not 295A. and why table 2 is needed at all if the procedure for calculation is right.
I think I am missing something between multiconductor cables and single conductors.
Any help and references would be highly appreciated.
Regards,
Newcomer2005