mgtrp
Electrical
- May 4, 2008
- 326
I'm looking for guidance on sizing of cables between the generator terminals and its associated excitation transformer. I'm specifically concerned with short-circuit withstand, as the fault currents at the generator terminals can be quite high in comparison to the size of the cable that would be used if ampacity were the only consideration. Some specific questions I have are:
[ol 1][li]Is short-circuit withstand normally a consideration? I know that it is omitted for short lengths of conductor such as jumpers from the busbar to VTs within switchgear, but I don't think that it should be for a longer cable that leaves the switchgear (in this specific case, approx 30-50m).[/li]
[li]Should the fault clearing time used in the cable heating calculation account for breaker fail, or assume that the protection operates correctly?[/li]
[li]Is any consideration given for generator run-down--i.e, the generator continuing to feed a fault even after the main and field breakers have tripped.[/li]
[/ol]
If it makes a difference, this is for a utility application under IEEE standards so NEC etc do not strictly apply. I'd be particularly interested in any standards or written sources that I could refer to.
Thanks in advance,
mgtrp
[ol 1][li]Is short-circuit withstand normally a consideration? I know that it is omitted for short lengths of conductor such as jumpers from the busbar to VTs within switchgear, but I don't think that it should be for a longer cable that leaves the switchgear (in this specific case, approx 30-50m).[/li]
[li]Should the fault clearing time used in the cable heating calculation account for breaker fail, or assume that the protection operates correctly?[/li]
[li]Is any consideration given for generator run-down--i.e, the generator continuing to feed a fault even after the main and field breakers have tripped.[/li]
[/ol]
If it makes a difference, this is for a utility application under IEEE standards so NEC etc do not strictly apply. I'd be particularly interested in any standards or written sources that I could refer to.
Thanks in advance,
mgtrp