Cable sizing with ETAP - SD starter

Status
Not open for further replies.

LDKGR

Electrical
Nov 4, 2014
41
Hi everyone,

I am trying to model in the ETAP a SD starter and size the supply cables of a motor (6 + PE). Do you have a good idea ?

Thanks
 
Replies continue below

Recommended for you

ETAP is not really a design tool. Sizing the conductors is something typically governed by local jurisdictional code requirements. As a generalized rule though, the 6 conductors are often allowed to be sized at 58% of the motor FLA.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 
Hi jraef, thanks for your reply but what do you mean "ETAP is not really a design tool" ?
In ETAP you can find a complete section of cable sizing.
 
Maybe so. But ETAP is really a modeling tool. Designing a system is a combination of modeling plus adjusting to site conditions and regulatory constraints. Computer programs are not good at that, yet.

When they are, we are all in trouble...[flush2]


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 
Jraef I agree with you but you can realize that I am trying to find how I can model this stuff in the ETAP.
 