Dandel,
My friend, I completely agree your statement that a DC HIPOT test is much cheaper than a PD test. I also acknowledge that I was not correct to directly compare DC HIPOT to 4 to 5x to AC HIPOT of 2x.
--DC HIPOT is cheaper than PD Test
Have you ever heard the old adage “You get what you pay for.”
--AC vs. DC HIPOT
An AC HIPOT is a much more robust HIPOT. The changing polarity allows PD to show up at a much lower voltage.
I respectfully disagree that a DC HIPOT test performed at any voltage is as good as AC PD test. In our 10,000km of cable testing experience we have seen many cables pass the DC HIPOT test, but completely fail the PD test.
---The human ear can not hear many serious PD sites.
In order to hear a PD the magnitude must be in the 1000s or 10,000s of pC. If one uses an ultrasonic sensor you may be able to 'hear' PD as small as 100pC. IEEE 48 termination specification states for a properly built termination can not have even a few pC at around 1.4Uo. It is not the magnitude of the PD that will brake down the cable/termination, but rather the pressure per unit area! A termination with continuous PD at operating voltage with 50pC of magnitude will fail the cable eventually. If the 50pC is over a small area the termination will fail much quicker than if it is distributed over a large area. If a termination fails 10years later, does anyone fault the workmanship? The contractor’s 1 year warranty is long gone!
--PD Test can find much more DC HIPOT tests
DC HIPOTs detect leakage – tracking/conduction –resistive currents. The defects that a PD systems can see and locate range from tracking (conduction), which DC can find, to defects that will only cause failure after years of material degradation, such as voids. A void in layers of a modern heat shrink or cold shrink termination is not likely to be picked up by a DC HIPOT test because there is very little leakage current in the high impedance defect. The largest component of the current due to PD in a void is capacitive. One has to measure pico Amps to find many serious defects!
--The old days
Back in the old days when terminations were made by hand with semiconducting tapes, tracking/conduction was a much bigger issue. The DC HIPOT was also useful for PILC cables, again because conduction losses are what cause many of the failures.
--New tools for moderns systems
Modern PD systems can easily identify defects with PD from a few pC to greater than 10,000pC. Some modern terminations are resistively graded. This means they will naturally have a leakage current. If one use modern diagnostic techniques for modern systems I sure you will find many more workmanship errors than .1%.
If a cable system owner would like to be sure their system will be reliable for years to come a comprehensive PD test is a small price to pay. Cable, termination, and joint manufactures will tell you that the best test commissioning test is a PD test. This is what they do in the factory. Why not use this baseline in the field?
-Cheers!