I am curious about the "Cable Tray (CT) Rating” in accordance with the NEC.
What peaked my curiosity about this rating is when I was looking at a mining application for a portable 30m conveyor. The conveyor requires 5kV flexible cable for its power feed.
The CT rating was required because the cable was going into a cable tray alongside the conveyor. However you won't find a flexible, 3 conductor mining cable (with ground check) @ MV that is CT rated and MSHA approved. How come? You would think that a cable used for portable equipment such as trailing cable for shovels, draglines, etc, would be built way more robust than a cable that you place in cable tray for protection?
Also on a side note, why aren't most power MV cables CT rated until you get above 1/0AWG?
The best article I could find on cable tray rating is this:
It states, the cable tray rating tests for: "flammability and other mechanical (including a crush test) and temperature tests" that allow them to be marked cable tray rated." However, aren't many cables that don’t have the rating, tested in similar fashion? The article didn’t describe why most MV cables aren’t CT rated until you get buy larger than 1/0AWG diameter conductors.
What peaked my curiosity about this rating is when I was looking at a mining application for a portable 30m conveyor. The conveyor requires 5kV flexible cable for its power feed.
The CT rating was required because the cable was going into a cable tray alongside the conveyor. However you won't find a flexible, 3 conductor mining cable (with ground check) @ MV that is CT rated and MSHA approved. How come? You would think that a cable used for portable equipment such as trailing cable for shovels, draglines, etc, would be built way more robust than a cable that you place in cable tray for protection?
Also on a side note, why aren't most power MV cables CT rated until you get above 1/0AWG?
The best article I could find on cable tray rating is this:
It states, the cable tray rating tests for: "flammability and other mechanical (including a crush test) and temperature tests" that allow them to be marked cable tray rated." However, aren't many cables that don’t have the rating, tested in similar fashion? The article didn’t describe why most MV cables aren’t CT rated until you get buy larger than 1/0AWG diameter conductors.