Cable Tray Rung Spacing

Status
Not open for further replies.

Humble2000

Electrical
Nov 17, 2005
132
Dear Friends,
Is there a formula to calculate the ladder type cable tray
rung spacing?
I know that they come in 6"-9"-12"-24" spacing and 12" is most popular;however what is the rule of tumb or formula that is used for this purpose?
Any feedback is apprceited.

 
Replies continue below

Recommended for you

If you are using the 2002 or 2005 NEC the cable article number is 392. Many of the Chapter 3 articles were re-numbered for the 2002 edition of the NEC.
Don
 
I would also refer to the Cable Tray Institute's site:
For practical consideration, single conductors #1/0 to #4/0 may only be installed where the rung space is 9" or less. See [NEC 2005]392.3(B)(1)(a). Otherwise I know of no particular restrictions.
 
Try this link.
NEMA said:
STANDARDS
NEMA STANDARDS
VE 1-1991
REV. NOVEMBER 1993
Scope
This standard covers continuous, complete, metallic systems of ladder,
trough, solid-bottom or channel cable tray intended for, but not limited to,
the support of power, control and signal cables.

NEMA STANDARDS said:
4. Rung Spacing on Straight Sections - 6", 9", 12", or
18" (152mm, 229mm, 305mm, or 457mm) on centers.
5. Radii - 12", 24", and 36" (305mm, 610mm, and 914mm).

18" spacing may not be available from all manufacturers.
yours
 