Caisson uplift 1

Status
Not open for further replies.

wildehond

Structural
Mar 24, 2006
54
We're planning to recommend the sinking of a concrete caisson for a large sewerage manhole. During winter, it is likely that the water table could rise 8 meter above the bottom of the caisson. Two questions:

1. In the equilibrium calculations, when comparing gravity stabilising forces versus buoyancy, what would be a reasonable factor of safety to use? Should the dead load be 10% more than the buoyancy? Or more?
2. Is there a convenient "skin friction" that can be used to calculate the resistance to uplift. This to be added to the deadweight to improve the Factor of Safety.

Thanks
Alten Hulme
 
Replies continue below

Recommended for you

I would ignore skin friction unless you have a competent geotech tell you that you can with saturated soil.

Usual building code combination is 0.6D + W for uplift/overturning with wind. For buoyancy I'd use the same (0.6D + Buoyancy). Others use a SF of 1.5 as well. Very similar.

 
JAE

Thanks for your reply.

1. Yes, the skin friction one does seem a bit iffy, but I'm trying hard to reduce the concrete required.
2. 0.6D seems conservative in that:
2.1 The dead load can be accurately determined
2.2 The water table height being used in the calculation is a conservative height.

For now

Alten


 
I think the 0.6D has more to do with the 1.5 safety factor on 0.9D. Something like a Caisson floating away is pretty catastrophic, so a 1.5 FS is a minimum at best. Think about it: compared to most strucutral calculation, this one has no material safety factor built in... it's not like designing a wood beam to 90% or 95%. It's merely taking physics: and so, the 1.5 FS is not necessarilt the case in which you have 60% dead, but actually, for the case where you have an extra 50% of pressure due to unforeseen circumstances... like a flood, hurricane, etc.

Good luck!
Mike
 
Mike

thanks. You've put it in perspective.

Alten
 
If you assume your foundation is submerged, it seems to me that bouyancy is then a type "F" load, "load due to fluids with well defined pressures and maximum heights." I don't see that ASCE7, article 2.4 calls for 0.6D + Bouyancy.
 
Yes, I think Mike is correct that 0.6D is more of a safety factor on the event rather than a response to uncertainty in the dead load.

 
You could reduce the concrete dead weight (i.e., volume of concrete) by using tie-down anchors through the bottom of the caisson.
 