Hello,
This web page
says:
Then what does? It seems that they try to explain:
If there is a maximum acceptable ceiling-temperature value and a minimum acceptable supply air temperature, then a given total cooling load (regardless of how the cooling load is distributed by elevation) seems that it is going to dictate the air flow rate.
Why wouldn't the overall room delta T and the sum of all heat gains (regardless of elevation) be the bases for calculating the air flow requirement?
Thanks,
Yittri
This web page
says:
Research indicates that stratification for UFAD systems can result in overall delta T's (return-supply temperature difference) in the range of 8-11°C (15-20°F), for properly designed systems. However, these values are not what determine the air flow requirement.
Then what does? It seems that they try to explain:
The heat gain to the occupied zone and the air flow required to maintain a given comfort condition in that zone is what determines the actual air flow requirements, and consequently the overall delta T that will be developed.
If there is a maximum acceptable ceiling-temperature value and a minimum acceptable supply air temperature, then a given total cooling load (regardless of how the cooling load is distributed by elevation) seems that it is going to dictate the air flow rate.
Why wouldn't the overall room delta T and the sum of all heat gains (regardless of elevation) be the bases for calculating the air flow requirement?
Thanks,
Yittri