Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Calculating Allowable Leakage for air tests on Control Valves

Status
Not open for further replies.

CarlosEstinos

Mechanical
Nov 24, 2011
31
Hello All,

I am calculating the allowable leakage for control valves using OEM stated Cv value that is a liquid coefficient.
Using the liquid Cv value, this gives me the allowable leakage as per the specific gravity of the fluid (in this case water)

How can you calculate the allowable leakage of a valve when doing an air test if you are using the liquid flow coefficient?

Any guidance or information would be much appreciated.

Thanks in advance


 
Replies continue below

Recommended for you

You really can't make an exact conversion, the flow regimes for the two leaking fluids are just too far apart. That said, some manufacturers use air testing for leakage because it is a more stringent test (air due to lower density, lower surface tension, and lower viscosity will in general leak at a greater volumetric rate than water), is quicker and easier to run with near zero "cleanup". Some manufacturers may have correlation data that will give equivalent water leak rates for a measured air leak rate, given a particular sealing design geometry and materials.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor