Calculating body heat off of children in a school

Status
Not open for further replies.

Netter1

Mechanical
Oct 19, 2003
15
Can anyone tell me what values (BTUH Sensible and Latent) I should be putting down for children in a classroom setting?
Thanks,
 
Replies continue below

Recommended for you

For a clasroom figure about about 45 to 50 BTU sq /ft
This is total heat, with a SH ratio of 70/80 %
 
There are tables which deal this issue specifically. Though the total heat load remains constant at 300btu/child, sensible and latent heats vary as per the room temperature.

Temp. SH LH
82F 180Btu/person 220Btu/person
80F 195Btu/person 205Btu/person
78F 215Btu/person 185Btu/person
75F 240Btu/person 160Btu/person
70F 275FBtu/person 125Btu/person

For children you should consider 75% of these values, for the above quoted numbers are for adult males.

Regards,


Believe it or not : Had we trusted Archimedes and assigned him the work of lifting the earth(or any mass equivalent to that of earth on earth),with a lever of suitable length, it would have taken him 23 million million years to lift the earth by one centimeter, if he worked at the rate of 1 HP.
 
Thank you for your help once again.
I sure appreciate it and am learning a lot from you all in here.
 