Calculating capacity of vertical overflow pipe in box gutter sump (example attached)

Status
Not open for further replies.

KlopferDobos

Civil/Environmental
May 8, 2017
1
0
0
AU
Hello,

I have a situation where we are installing a new gutter on an existing roof which was previously leaking and had no overflow provision. I have attached a detail of our proposal.

My question is...how do I go about calculating the capacity of the vertical overflow pipe in this situation? We have a 150mm deep sump with the overflow rising 184mm above the bottom of the sump (so 34mm above the bottom of the gutter).

Australian Standard AS3500.3 Section 3.7.5.2 states that "A vertical pipe overflow that projects through the floor of the sump, is a possible alternative where a high capacity device is not required. No equations, graphs or examples are provided for vertical pipe overflow devices due to a lack of appropriate research data."

Anyone haev any ideas? I'm guessing this would this would either be solved with:

(a) Circular weir equation? If so, what formula should be used? Or,
(b) Orifice equation?

Also, how would you determine what H value to use?

Thank you in advance,

Alex
 
 http://files.engineering.com/getfile.aspx?folder=74379406-9de5-4431-98cb-9b593e342723&file=Overflow.jpg
Replies continue below

Recommended for you

I would use the orifice equation, with the head being the distance from the top of the overflow pipe to the WSE in the gutter.

For low-head conditions you could compare this to weir flow, using the sharp-crested weir equation based on the perimeter of the orifice.