I may or may not have a delimma of sorts. I have a large rotating mass coupled to a gear reducer, hanging vertically from a ceiling. In the mounting structure, I have a 12,000 in.lb. torque cell. Assuming that the torque cell is properly calibrated (2 point scaling method used @ 150 ft.lbs max), I use the measured counter torque on the mounting structure to calculate the Motor HP required to drive the load. I've been using the following formula:
Motor HP= (((Output in.lbs.)/(Ratio*Eff.))*(Output RPM*Ratio))/63,000
Using this formula in an example with the following variables:
Motor NP HP = 1.5
Motor FLA = 2.8
Motor NP RPM = 1750
Reducer = 21.67 : 1
Reducer Eff. = 0.97
Measured Output Counter-torque = 389.1 in.lbs
Measured Output RPM = 83.5
VFD Output Frequency = 62.0 Hz
Measured Motor Current = 2.34A
When I plug the measured torque and speed into the above formula, I get a Motor Shaft HP of 0.532, but I also see that at 60Hz, my motor is loaded at 84% based on FLA.
For a 1.5HP motor loaded at 84%, my calculated value of 0.532 seems to be too low. It's making me feel funny about making assumptions for future testing based on these numbers. Would you guys disagree with my method?
Is there an alternate "electrical" method of calculating actual motor HP output, when Current, RPM, NP eff. are known, but voltage is not? I would naturally want to assume there isn't, since there's no good way to calculate power consumption on the motor leads because of PWM voltages.
I have a scope. I have a fluke 43B PQ analyzer, but I question accuracy because of the PWM content.
Help? Me? Thanks in advance guys (and gals)
Motor HP= (((Output in.lbs.)/(Ratio*Eff.))*(Output RPM*Ratio))/63,000
Using this formula in an example with the following variables:
Motor NP HP = 1.5
Motor FLA = 2.8
Motor NP RPM = 1750
Reducer = 21.67 : 1
Reducer Eff. = 0.97
Measured Output Counter-torque = 389.1 in.lbs
Measured Output RPM = 83.5
VFD Output Frequency = 62.0 Hz
Measured Motor Current = 2.34A
When I plug the measured torque and speed into the above formula, I get a Motor Shaft HP of 0.532, but I also see that at 60Hz, my motor is loaded at 84% based on FLA.
For a 1.5HP motor loaded at 84%, my calculated value of 0.532 seems to be too low. It's making me feel funny about making assumptions for future testing based on these numbers. Would you guys disagree with my method?
Is there an alternate "electrical" method of calculating actual motor HP output, when Current, RPM, NP eff. are known, but voltage is not? I would naturally want to assume there isn't, since there's no good way to calculate power consumption on the motor leads because of PWM voltages.
I have a scope. I have a fluke 43B PQ analyzer, but I question accuracy because of the PWM content.
Help? Me? Thanks in advance guys (and gals)