Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Calculating negative pressure

Status
Not open for further replies.

emalsyd

Mechanical
May 10, 2006
43
Is there a calculation to determine how much exhaust is needed in a space to get a desired negative pressure. We have a room with 1200 supply cfm. They are looking for the room to always be a minimum of .01 wc negative. Need to determine how much cfm to exhaust.
 
Replies continue below

Recommended for you

Obviously, you have to exhaust more the 1200 CFM. Use the first law of thermo. developed for isothermal condition and such equation can be found in fluid dynamics textbooks; then you can use an inclined manometer to figure out how much of pressure differential you have between inside and outside the room.
 
Status
Not open for further replies.