33
I need to size a grinder pump for an Art Museum. Is there a way to estimate flows based on fixture count? Or could one use a certain gpm per square foot of building space.
Eveything I have found online references flow calcs based on residential flow.
 
Replies continue below

Recommended for you

You will get the most accurate estimate if you use the fixture count method.
 
The Art Museum has 5 sinks, 1 mop sink, 9 lavatorys, 8 toilets, and 2 urinals. What are the flow vales assigned to these type of fixtures?
 
Your local plumbing code will tell you exactly that.
 
Lavatory = 2 DFU
Water Closet = 4 DFU
Sink Service = 2 DFU
Urinal Pedestal = 6 DFU
Mop Sink = 2 DFU

2 DFU = 1 GPM.

Reference: Piping Handbook

These numbers will vary somewhat on the type of fixture and the age of the fixture. Newer fixtures will use less water.
 