callawaygolfer
Structural
- Oct 18, 2004
- 7
I need help in calculating the water flow rate in pipe line project.
Given:
1. Tapping into the city's 8" water main.
2. Measured flow rate of 1550 gpm and 78 psi just upstream of the tap point, measured at a fire hydrant. By my calculation you have 181.52 feet of head available at the tap point.
3. Adding a new 6" water line to feed the building water service requirements. Using 6" cement lined ductile-iron pipe below grade outside the building and 6" PVC pipe inside the building.
4. The 6" line will dump into a well that feeds our cooling water system. Water flow rate needs to be at least 1000 gpm. This system will only be used rarely, so the 11.4 fps flow velocity isn't much of a concern.
5. Including pipe bends the total length of ductile iron pipe is 450 feet and the PVC it's 375 feet.
6. Head loss through valves & back flow preventers is about 70 feet.
7. I've been using a Hazen-Williams constant (C) of 140 for both pipes.
I know to use Bernoulli's equation, but I keep getting the velocity at the well is much greater than at the water main, which to me doesn't make since unless the pipe is no longer flowing full.
Not finding much on the internet to help either.
I'm assuming the pressure head at the well is 0 feet.
This is out of my area of expertise and it's been awhile since I studied fluid mechanics in school, plus I've seen to have misplaced (or had stolen) my fluid mechanics reference books.
Any help would be appreciated.
Given:
1. Tapping into the city's 8" water main.
2. Measured flow rate of 1550 gpm and 78 psi just upstream of the tap point, measured at a fire hydrant. By my calculation you have 181.52 feet of head available at the tap point.
3. Adding a new 6" water line to feed the building water service requirements. Using 6" cement lined ductile-iron pipe below grade outside the building and 6" PVC pipe inside the building.
4. The 6" line will dump into a well that feeds our cooling water system. Water flow rate needs to be at least 1000 gpm. This system will only be used rarely, so the 11.4 fps flow velocity isn't much of a concern.
5. Including pipe bends the total length of ductile iron pipe is 450 feet and the PVC it's 375 feet.
6. Head loss through valves & back flow preventers is about 70 feet.
7. I've been using a Hazen-Williams constant (C) of 140 for both pipes.
I know to use Bernoulli's equation, but I keep getting the velocity at the well is much greater than at the water main, which to me doesn't make since unless the pipe is no longer flowing full.
Not finding much on the internet to help either.
I'm assuming the pressure head at the well is 0 feet.
This is out of my area of expertise and it's been awhile since I studied fluid mechanics in school, plus I've seen to have misplaced (or had stolen) my fluid mechanics reference books.
Any help would be appreciated.