Calculation of distributed load on beam
tayldan
1
I'm unsure how to find the distributed load acting on the highlighted beam. The floor load is know (2.4 kPa live load + 5.4 kPa self weight) but I'm unsure what tributary width should be used to determine the distributed load on the beam in kPa.
You can do a very simple area assignment as a rough order of magnitude (essentially half the P7), but for detailed design because of the combination of columns and walls I would model this in a suitable structural design programme.
You can calculate assuming tributary load distribution. You may search the web for ( slab tributary load distribution) or look to the old reinforced concrete books. I searched the web and one of the outcomes . ( Structville ,Ubani)
In your case , if n for service loads = 5.4 kPa +2.4 kPa =7.8 kPa ,
Max load ( ht of triangular loading ) qmax=( 6/2)*7.8=23.4 kN
UDL ( equivalent uniform load of triangular load) q= (6/3)*7.8 =15.6 kN/m ( this UDL could be used for support moments )
Nowadays , almost everybody will prefer to model with FEM and find more precisely.