Hi all. I'm new here, nice to be here. I can start with stating that I'm not a student. At my job I do adjustments of ventilation systems, all done with different types of flow meters. Now I thought I could do this theoretically in some way.
Overview
I have a question on how to theoretically calculate settings on valves/diffusers in a ventilation system (air).
I have made a simple example overview of the situation in the picture below. I know what the output from the diffusers SHOULD be (that's QP in liter/sec), I know the size of the pipes (stated in the picture).
When you adjust a valve/diffuser in a ventilation system, you normally change the k-factor to get the correct flow, a little bit of trial 'n error, you lower the k-factor to get a lower flow (vice versa for the opposit of course) and see if it's close to QP (What flow you want to have there). The formula looks like this:
Q is the flow in liter/sec, and I know what I want here (it should say QP, but it doesn't matter). K is the k-factor for the diffuser, a diffuser has many different k-factors. At last we have DeltaP which is the differential pressure.
Problem
Calculate what k-factor the diffusers should have to get the correct flow (QP). We know QP(Q), we want the K. So I guess we need the DeltaP? Maybe the k-factor isnt enough, maybe I need to know the effective area on the diffuser?
I guess the total flowrate of the fan would also be good to know.
Thoughts
I have read some fluid mechanics, but I don't know how to put all pieces together. I have some theory on how to calculate it though:
1. Get velocity (dividing volumetric flow rate by cross-sectional area)
2. Calculate the pressure loss per some unit length
3. Calculate the total length (with bends etc)
4. Calculate the total pressure loss.
----
The problem with my example is that the pipes get smaller from the MP (MainPipe), I guess the bernoulli's equation would be used here.
Last thoughts
If it's something more you need to know about this example, just assume some values. Thank You.
Example
Overview
I have a question on how to theoretically calculate settings on valves/diffusers in a ventilation system (air).
I have made a simple example overview of the situation in the picture below. I know what the output from the diffusers SHOULD be (that's QP in liter/sec), I know the size of the pipes (stated in the picture).
When you adjust a valve/diffuser in a ventilation system, you normally change the k-factor to get the correct flow, a little bit of trial 'n error, you lower the k-factor to get a lower flow (vice versa for the opposit of course) and see if it's close to QP (What flow you want to have there). The formula looks like this:
Q is the flow in liter/sec, and I know what I want here (it should say QP, but it doesn't matter). K is the k-factor for the diffuser, a diffuser has many different k-factors. At last we have DeltaP which is the differential pressure.
Problem
Calculate what k-factor the diffusers should have to get the correct flow (QP). We know QP(Q), we want the K. So I guess we need the DeltaP? Maybe the k-factor isnt enough, maybe I need to know the effective area on the diffuser?
I guess the total flowrate of the fan would also be good to know.
Thoughts
I have read some fluid mechanics, but I don't know how to put all pieces together. I have some theory on how to calculate it though:
1. Get velocity (dividing volumetric flow rate by cross-sectional area)
2. Calculate the pressure loss per some unit length
3. Calculate the total length (with bends etc)
4. Calculate the total pressure loss.
----
The problem with my example is that the pipes get smaller from the MP (MainPipe), I guess the bernoulli's equation would be used here.
Last thoughts
If it's something more you need to know about this example, just assume some values. Thank You.
Example