On 29 Mar 05 12:50 BigH (Geotechnical) wrote, "Neville's paper was in Concrete International - about 2001 or 2002, I believe - I have a copy and will look it up tomorrow."
Did you ever find this? I've looked and can't find it.
Similar to the thread 592-119191 we are having a problem with 6000psi concrete on a particular job.
The commentary in ACI 318-02 states: R 5.6.5 A core obtained through the use of a water-cooled bit results in a moisture gradient between the exterior and interior of the core being created during drilling. This adversely affects the core’s compressive strength. The restriction on the commencement of core testing provides a minimum time for the moisture gradient to dissipate.
Don’t large masses of concrete duplicate this sort of moisture gradient, not by wetting the exterior but just due to its mass retaining heat/moisture on the interior? Say you have a concrete column 26” x 26” x 14’. Since mass traps heat and moisture and heat and moisture cures concrete, should one expect higher peak heat and moisture closer to the interior of the column and that this interior condition may translate into a higher compressive strength from a core sample from the interior of a column? Is a 26"x26"x14' column big enough to cause this gradient or is this legalistic hair splitting?
Cores were taken and they were 1500 psi higher than the our cylinders. Cylinders are running between 4500 and 5000 at 28 days and cores are running 6000 to 7000. I pointed out concreteguru's opinion that taking one long core and cutting it into three specimens does not best represent an average of the in-situ strength of the concrete member and that the objective would be better served by random sampling core locations and then averaging the results.
FYI, no initial curing at job site in very hot weather 95F+ daily and no one understands why low breaks. Go figure.
Did you ever find this? I've looked and can't find it.
Similar to the thread 592-119191 we are having a problem with 6000psi concrete on a particular job.
The commentary in ACI 318-02 states: R 5.6.5 A core obtained through the use of a water-cooled bit results in a moisture gradient between the exterior and interior of the core being created during drilling. This adversely affects the core’s compressive strength. The restriction on the commencement of core testing provides a minimum time for the moisture gradient to dissipate.
Don’t large masses of concrete duplicate this sort of moisture gradient, not by wetting the exterior but just due to its mass retaining heat/moisture on the interior? Say you have a concrete column 26” x 26” x 14’. Since mass traps heat and moisture and heat and moisture cures concrete, should one expect higher peak heat and moisture closer to the interior of the column and that this interior condition may translate into a higher compressive strength from a core sample from the interior of a column? Is a 26"x26"x14' column big enough to cause this gradient or is this legalistic hair splitting?
Cores were taken and they were 1500 psi higher than the our cylinders. Cylinders are running between 4500 and 5000 at 28 days and cores are running 6000 to 7000. I pointed out concreteguru's opinion that taking one long core and cutting it into three specimens does not best represent an average of the in-situ strength of the concrete member and that the objective would be better served by random sampling core locations and then averaging the results.
FYI, no initial curing at job site in very hot weather 95F+ daily and no one understands why low breaks. Go figure.