Dear Mr Dvhez 2 Apr 19 11:50
A1. I was expecting for the clarification, but to no avail so far (5/4/2019).
Dear Mr waross
Info: " Are you asking about the output fault current of a VFD or the maximum allowable fault level of the supply system? 100 kA seems a little high for a VFD output."
A2. It is unlikely for any one to install [any] form of short-circuit protective device(SCPD) between the VFD [out put] and the motor. Therefore, the 3-phase or 1-phase kA ratings at the [output] of the VFD may? not be the question asked.
A2.1 However, it is a [must] to have a (SCPD) placed at the [input] i.e. ahead of the VFD, in order to protect it. Therefore, the rating of the (SCPD) must be adequately rated for the system short-circuit levels and shall have the characteristic recommended by the manufacturer, in order to protect the VFD.
FYI: the SCPD recommended by the manufacturer must be respected in order to protect her device; the manufacturer knows better.
Che Kuan Yau (Singapore)