I know there are some threads talking about circuit switchers. But what the problems is that our Chief engineer said CS is not designed to interrupt fault currents therefore, can not be used to clear a fault which I believe it is B.S.

Since we have a 66kV line from a system substation A (230/66kV)connecting to a 66kV substation B(66/25kV) - a transformer with a high side CS and low side a 25kV CB to drop the transformer during a transformer fault and if the fault current is to be beyond the CSs rating then the protection will close a 66kV ground switch and trip substation A side CBS of the 66kV line.
What I know is that CS can interrupt the fault current but with lower interrupting rating compare to the CBs. Can anybody give some specific interrupting ratings of CSs on 66/69kV level?

Thanks in Advance!
 
Replies continue below

Recommended for you

Pick the right circuit switchers and you can get close to or match breaker interrupting ratings. Circuit switchers are not designed to accommodate bushing CTs nor are they designed for rapid reclosing. Other than that some are difficult to distinguish from breakers based on ratings.
 
The short answer is "Yes" but has either limited interrupting capability or limited number of shots
 
Look on the S&C and Southern States web sites for technical details. As is mentioned above...your boss is not correct.

 
Thanks Gentlemen and pleased to get everybody's helps
Regards,