bdn2004
Electrical
- Jan 27, 2007
- 794
There is a new 12.47kV primary line being fed into a new 15kV power circuit breaker with a 751SEL relay. The power circuit breaker feeds a 2500kVA outdoor pad mounted transformer. The transformer is a 2500kVA, Delta-Wye, solidly grounded, 12.47kV-480/277V. The transformer feeds a low voltage switchgear that's located about 50' from the transformer inside.
We have a proposal where he's showing 3 - 200/5 CTs on the primary, and CT's on the secondary. And he's calling that differential protection that will protect the switchgear. We weren't expecting the secondary CT's. Is this a common installation now ?